MICHAEL WATKINS | Seattle C…
City Light has no comments on this section of the BP.
Shell Energy opposes the requirement that aggregated qualified resources less than 1 MW be located within 10 miles of each other. It appears this will disqualify many behind the meter resources unnecessarily from providing benefits to the participating resource owner/contract holder and the wider program footprint.
WILLIAM GODDARD | Calpine E…
Agree with Shell. Delete language after first sentence. Connectivity to common trnamission injection point should be sufficient.
KATIE NELSON | BPA
- 2nd paragraph - '...in close proximity...' - This feel pretty arbitrary. For one the PO could decide 50 miles is close enough for another it needs to be within 25? Guidelines would be good.
CONNOR CURSON | Powerex
LEAH MARQUEZ-GLYNN | Tacoma Po…
Please identify the means by which the following should be communicated “For Qualifying Resources that are requested to be aggregated, the following information should be provided to the PO.” Can this be done within the Advance Assessment data request workbook?
KATIE NELSON | BPA
LORI HERMANSON | Avista
Need to include instructions on how to handle aggregation of <1 MW resources that are not located with either a 10 mile radius or two electrical buses, whichever is shorter.
TYLER MOORE | Arizona P…
No comment on this section.
LINDSEY SCHLEKEWAY | NVE
AMY BURTON | PSE
CAMILLE CHRISTEN | Idaho Pow…
BENJAMIN FAULKINBERRY | PacifiCor…
JERRET FISCHER | SRP
No comment at this time.